Determining length of black pipe
Jeff_17
Member Posts: 99
When I measure a section of Black pipe for steam or other purposes BETWEEN two fittings ....let's say two elbows....If the distance between the elbows is 9 inches...what should be the length of the black pipe nipple between them?
0
Comments
-
Depends on diameter...
0.5" is 0.53"
0.75" is 0.55"
1" is 0.68"
1.25" is 0.71"
1.5" is 0.72"
2" is 0.76"
3" is 1.20"
4" is 1.30"
0 -
Length Of Pipe
Remember that if you're running between things like a pair of 90*s, you'll need a union somewhere.
Consider finding a copy of Audel's "Mechanical Trades Pocket Manual". It has a load of really good information on a broad range of technical subjects, and among it is a table for the "Take Aways" for screwed fittings.0 -
Hold on....
This is simple.. I have 3/8 in pipe that I need to join. I understand that I need unions, etc...BUT I just need what EXTRA lenght I allow for the length of pipe that is actually screwed into the elbows, unions, etc....for example...if it is an 8 inch nipple..do I CUT/BUY 8.5 in nipple..or longer?0 -
3/8\"
Normal depth for tight joint is 0.41" at each end. You'll need a piece about 8.8" long.0 -
Now...
i understand!!! Thanks sooo much!0 -
The Total...
...make up for each 3/8" thread will be 7/16". So for two fittings, you'd need to add 7/8" to your length. If a union has to go in, then the take-away or take-off is 7/8". This means your end-to-end length of pipe is 8 - 7/8". Take away for a union, if required, and the total length is 8". You need two nipples totalling 8" long - one each side of the union. It just happens with this pipe size that the two values cancel each other out. A pair of 4", a 5" and a 3" - doesn't really matter. It won't necessarily work out this way with all pipe sizes or fittings, so don't assume. If you don't need a union in this piece of pipe, then it's 8 - 7/8" end to end.
To keep it straight, it's often better to work centre to centre or end to centre, then everything is a subtraction.0 -
That helps EVEN...
> i understand!!! Thanks sooo much!
0 -
That helps EVEN...
MORE!!! I do need one union to join to lenghts. Forgt what size, but I can figure it out from what you have said!0
This discussion has been closed.
Categories
- All Categories
- 86.6K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 54 Biomass
- 423 Carbon Monoxide Awareness
- 98 Chimneys & Flues
- 2K Domestic Hot Water
- 5.5K Gas Heating
- 101 Geothermal
- 157 Indoor-Air Quality
- 3.5K Oil Heating
- 66 Pipe Deterioration
- 931 Plumbing
- 6.2K Radiant Heating
- 384 Solar
- 15.2K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 43 Industry Classes
- 48 Job Opportunities
- 17 Recall Announcements