I had an incident where my Lennox oil-fired boiler ran with out water in the pipes (dry fire). Since I was not home at the time, it ran long enough and got very HOT and is now ruined. Besides the aquastat, are there any safety features on a boiler to shut it off if it overheates in a situation like this? Seems like relying on only the aquastat is risky as the boiler has to get pretty hot in order get the aquastat up to temp with no water in the pipes.

Thanks.

Comments

  • Pinball
    Pinball Member Posts: 249


    It's called a Low water cut-off and is now code in NYS.on all boilers, residential and commercial

    Al
  • Robert O'Connor_7
    Robert O'Connor_7 Member Posts: 688
    LWCO..

    Pinball's right, and if your boiler were really big, you would need two..Robert O'Connor/NJ
  • Mijola
    Mijola Member Posts: 124
    Dry fire boiler

    Is the boiler a steam boiler or a forced hot water heating boiler?

    Regards,

    Ed
  • Ralph_3
    Ralph_3 Member Posts: 2


    The unit is forced hot-water heating, i.e., it has a circulating pump.
  • Weezbo
    Weezbo Member Posts: 6,231
    sounds like a LWCO is a good thing....

    on the boiler or associated piping within 6" of the boiler with no valves ahead of it,with a air relife and automatic fast fill...although maybe some larger ones might be better off with two and an additional high limit safety..
  • Sweet_2
    Sweet_2 Member Posts: 143
    Question ???

    LWCO seems to be concensus , would a flow switch suffice as well?
  • Steamhead
    Steamhead Member Posts: 17,638
    Good Idea

    combined with a LWCO, a flow switch shold provide additional protection. The only exception would be on a boiler that has a tankless coil, where the burner would have to fire without water flowing thru it.

    To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"
    All Steamed Up, Inc.
    Towson, MD, USA
    Steam, Vapor & Hot-Water Heating Specialists
    Oil & Gas Burner Service
    Consulting
  • Pstef
    Pstef Member Posts: 5
    Where does six inches come from


    Weezbo,

    Why do you say within six inches?

    Needs to be located above minimum safe water level available for boiler, which is indicated by boiler manufacturer. Make sure there is no shut-off valves located between the LWCO and the boiler, in order to prevent isolation of the boiler from the LWCO.

    My LWCO is located in the Primary loop about two feet above the boiler, no shutoff valve between boiler and LWCO. This way the LWCO will cut out way before level of boiler water beomes to low for dangerous operation.
  • Weezbo
    Weezbo Member Posts: 6,231
    the deal is theres the code, theres the man recs,and then

    theres your standards. you want to run the wires two feet up the wall thats fine ...i have no problem with that. i have no problem with having a pressure relife valve on the incomming water ,and on the boiler, either .one of them is code,the other well it is my preference with larger boilers.in some things i am an extremist :)the flow switch is a great idea too.