Reset Ratio/Parallel Shift Settings

New Viessmann Vitodens 11-44 boiler to replace the old cast iron boiler in a 4,000 [] house near San Francisco.

<A HREF="http://www.heatinghelp.com/getListed.cfm?id=53&Step=30">To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"</A>

Comments

  • High ceilings,

    lots of glass (all single-glazed) and a central atrium that acts as a chimney to pull the heat out. Stand next to it and you feel cold.

    To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"
  • Framing

    The house sits suspended over a ravine on a steel framework. No underfloor insulation.

    Our design temperature here in the Bay Area is 36°.

    The existing system is copper tube radiant in the slab floor. I have no idea what the spacing is.

    Given this information, what would your reset ratio and parallel shift settings be?

    To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"
  • jerry scharf_2
    jerry scharf_2 Member Posts: 414
    Heating calcs

    Alan,

    I assume you did a heat loss calc on the house at design temp. Since you have a pretty good guess at the radiant surface, you should be able to figure out the water temp required for the design day. Do the same thing with a design temp of 55, and that should give you a first approximation of the reset curve.

    jerry
  • hydronicsmike
    hydronicsmike Member Posts: 855
    IF it was a tekmar....

    I could help you out, but.........

    Just kidding. Give me a call and I'll help you anyways.

    Mike
  • hydronicsmike
    hydronicsmike Member Posts: 855
    Formula to calculate

    Heating Curve Or Reset Ratio = [Design Supply Temp - Room Temp (usually 70°F) ] Divided by [Room Temp (usually 70°F) - Outdoor Design Temp].

    Example:

    180°F Dsgn Sup - 70°F Divided by 70°F - 20°F (??) Out Dsgn = HC of 2.2


    Hope this helps.

    Mike
  • I wanted to

    see what you guys thought the numbers would be based on the characteristics of the house. All of the rooms were between 35-40 BTU's/[] and the hardwood floors didn't seem as though they would hinder heat transmission into the rooms.

    The original settings I used were a reset ratio of 1.0 with a parallel shift of 5° C. This wasn't able to keep up with the heat loss; I'm now up to 1.2 (reset ratio) and 15° C (parallel shift) and the boiler now seems to be able to get a grip on being able to heat the house.



    To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"
  • Mike T., Swampeast MO
    Mike T., Swampeast MO Member Posts: 6,928


    IMHO ratio is too high and the system hasn't had time to stabilize. You're going to need quite a bit of parallel shift.

    Go back to 1.0 ratio with shift at your current setting. Set ALL of the t-stats ABOVE the desired room temp and let the room temp setting of the boiler rule for at least two solar cycles. See what happens and I bet you can figure out the original layout/balance of the system...

    If the cantilivered sections still prove too cold, I'd flatten the curve and add more shift. If you steepen the curve I have a sneaking suspicion that the system return temp will try to climb.