I am servicing a low press steam system. I find alot of heat not working properly. Loaded with water is the biggest problem. After working on the traps and they are ok, they seem to stop heating again. There are no air vents on the cast heat. Is this the problem? Thanks.
0
Comments
-
This might be a Vapor system
Have you located any manufacturer's info on the radiator valves or traps, or any odd-looking devices in the piping around the boiler? If so, this would help us identify it.
The first thing to look for is- how does the air vent from the system? In most of these systems there is a centrally located air vent somewhere near the boiler, on the dry (overhead) return line. If this vent goes bad, the system won't heat well.
Also look for radiator traps piped between the ends of the steam mains and the dry returns. These act as air vents for the steam mains. If one of these is leaking, it will let steam into the dry return and the system won't heat well- just as if you had a bad radiator trap somewhere.
Take some pics and post them if you can.
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements