Welcome! Here are the website rules, as well as some tips for using this forum.
Need to contact us? Visit https://heatinghelp.com/contact-us/.
Click here to Find a Contractor in your area.
pump head

Robert O'Connor_3
Member Posts: 272
Last convector on loop doesn't get hot. Taco 110 on return side of boiler. 1-1/4 mains with 1/2" branches. Pump should be on boiler supply. Taco 110 pump to small??? It's har to believe.
My math
1-1/4" pipe good for 14 gpm
Longest circuit about 150 ft. =
150 ft + 50% * .04 = 9 ft head
Taco 110 max out at about 7 ft head for 10 gpm
Taco 007 is good for 6 gpm @ 9 ft head
Taco 0010 is good for 19 gpm @ 9 ft head
Is taco 0010 the right pump for me??
Please help
My math
1-1/4" pipe good for 14 gpm
Longest circuit about 150 ft. =
150 ft + 50% * .04 = 9 ft head
Taco 110 max out at about 7 ft head for 10 gpm
Taco 007 is good for 6 gpm @ 9 ft head
Taco 0010 is good for 19 gpm @ 9 ft head
Is taco 0010 the right pump for me??
Please help
0
Comments
-
Here is the curve on a 1100
This discussion has been closed.
Categories
- All Categories
- 86.7K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 56 Biomass
- 423 Carbon Monoxide Awareness
- 104 Chimneys & Flues
- 2K Domestic Hot Water
- 5.6K Gas Heating
- 103 Geothermal
- 159 Indoor-Air Quality
- 3.6K Oil Heating
- 69 Pipe Deterioration
- 942 Plumbing
- 6.2K Radiant Heating
- 385 Solar
- 15.3K Strictly Steam
- 3.4K Thermostats and Controls
- 54 Water Quality
- 43 Industry Classes
- 47 Job Opportunities
- 18 Recall Announcements