Yet another Main Vent Sizing Question
BD Brannan
Member Posts: 3
We have recently moved into a 90 year old home with steam heat. I've learned a lot from reading Dan's books and visiting the Wall (it's addictive), and I have been tweaking the system step by step, new vents, pitching rads, etc. But the amount of hissing and wheezing, especially upstairs, suggests that our main vents may be inadequate. I think they may be partly clogged, too.
Anyway, the house has two 2-1/2 inch diameter steam mains, one is 65 feet long, the other is 55 feet long. Currently there is one pretty suspect looking Hoffman 75 on the end of each main. If I could get suggestions on the correct main vent sizes it would be much appreciated. If they are the right size then I'll go ahead and try cleaning them, but I figured I would see if I needed to do any additional work first.
Then - I can move on to the next opportunity for improvement.
Thanks,
bd
Anyway, the house has two 2-1/2 inch diameter steam mains, one is 65 feet long, the other is 55 feet long. Currently there is one pretty suspect looking Hoffman 75 on the end of each main. If I could get suggestions on the correct main vent sizes it would be much appreciated. If they are the right size then I'll go ahead and try cleaning them, but I figured I would see if I needed to do any additional work first.
Then - I can move on to the next opportunity for improvement.
Thanks,
bd
0
Comments
-
Steamhead has all the charts...but I would start with
atleast 2 Gorton #2s on each main. The faster the air gets out the better. Mad Dog
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"0 -
main vent size
you have roughly 2.5 cubic ft. of air in in those lines
a hoffman 75 removes 1.4 cubic ft. per min at 2oz of pressure. so basicly they are sized right but it will take 2 mins to get all the air out. or you could go with mad dogs ad vice and get the air out in like 45 secs0 -
Mad Dog nailed it
a Gorton #2 on each should get those mains full of steam in a super hurry.
www.gorton-valves.com
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0 -
Thanks Guys!
I can't wait to get this taken care of. Quick question though, Mad Dog sez 2 Gorton #2's each and Steamhead sez 1 #2. Any risk of noise or weirdness by going with two each? The mains are all happily and continuously pitched down from the boiler to the drip riser, so from what I have learned it may not be a big deal.
Thanks,
bd0 -
I don't think it's possible to over-vent those mains
two per main can't hurt. If you want, try one per main and see if they vent quickly, then add more if needed. I have a system with mains similar to yours running great with one per main.
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0 -
Thanks, Steamhead. I kind of thought that was the case but wanted to be certain.
Thanks again,
bd0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements