Taco circulator gaskets
Ken C.
Member Posts: 267
I replaced a Taco 007 circulator today. I prefer the red, flat gaskets, but I didn't have any in the truck, so I had to use the black, round gaskets that come with the circulator. I didn't have any leaks, but I would think the flat red gasket would be more reliable, since it has much more sealing area. I took a tour of the Taco plant a while ago, and a factory rep told me he likes to use both styles of gaskets together. I'm just curious what type of gasket most of you use, and has anyone ever had a problem with the round black gaskets that come with the circulator? How many of you always use new circulator flange bolts?
0
Comments
-
Ken , i agree with the factory guy.
0 -
.
i always replace the bolts if i have to change the whole pump--most times i just change the cartridge --i have run into problems with the black gaskets --on the Taco and B&G if the piping is real tight when used on sidearm oil heaters in commercial applications with 2" black pipe going to it --those i use the red rubber--but the red rubber does not hold up as long as the black never heard of using both though--if the piping is spreadable and the flanges are in good shape always use the black0 -
Flat gasket, or O-ring?
Apparently, there is still some confusion on which flange gaskets to use with the Taco 00 series cartridge type circulators. EPDM, O-rings with a square cross section are standard, and included with the circulators. This gasket has been proving to be a superior design, over the old red flat gaskets that can take a permanent seat when heated. When using taco shut off flanges, there is a flat black gasket included, and must be used with the o-ring included with the pump. Hopefully, this helps shed some light on which flange to use.
Taco, Inc.
Joe Mattiello
Technical Service Technician
joemat@taco-hvac.com
401-942-8000 X 484
www.taco-hvac.comJoe Mattiello
N. E. Regional Manger, Commercial Products
Taco Comfort Solutions0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements