replaced main vents, boiler flooded
mjbr24
Member Posts: 7
i just replaced 1 of 2 hoffman #4 main vents with Jacobus #1. The boiler fired up before i changed the second one because it's buried in the ceiling. i let it run and the boiler completely flooded up into the main lines. this has never happened before. (I am ordering Dan's book, BTW). I noticed on Hoffman's website that #4 vents are vacuum and #4A non-vacuum. I have gas heat, so I thought the #4s were always wrong and I needed a non-vacuum vent (Jacobus #1). Was the flooding because I only changed 1 vent and had a "bad" one still on the other main? should I be using Jacobus #1s?
0
Comments
-
Something else went wrong
Two possibilities are a leaking water feeder, or a blocked return line. The vents did not cause this.
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0 -
i just fired the boiler up again with the new vent after draining the water down. the water remained at the proper level and the boiler provided heat to all radiators before cycling off. if i had a blocked line, is it possible that it is clear now? thanks for the info. it's people like you who make this site great.0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements