two pipe steam boiler/Dunham air eliminator
Stuart_4
Member Posts: 1
I have a problem with a residential two pipe steam heating system. I found system off on pressure and creating a vacuum. At the end of the return is a Dunham Air Eliminator. Could this be the problem? Is this Air Eliminator really a steam or bucket trap? Can I repair or replace?
0
Comments
-
More likely, it is the old vacuum /air vent
on the dry return. I have seen the air eliminators and return trap get airbound. It can be removed, but you reallly have to know The Steam . Mad Dog
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"0 -
dunham air elininator
on the top of this air eliminator is a air vent, sorta of like a hoffman 500, w/the disc's. it constantly blows steam when the system is operating.I also took apart this air eliminator. it has a short rod and app.3"float. this float has liquid in it, and seems to rest/seal the bottom of this device. any thoughts? anyone?0 -
Mad Dog is right, it's an air vent
with a vacuum check disc on the outlet. The disc should be removed for oil or gas firing, since vacuum only worked well with coal. The float inside was there to shut the vent if water rose high enough that it might come out the vent.
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0 -
Steamhead is right on
He's a detail guy. alright! Mad Dog
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"0 -
mad dog's reply
so guys, are you telling me to eliminate the hole air elinimator, or just remove the guts, and reconnect it back to the system? do i need to put anything back in its place? by the way, this is a gas fired steam system and the boiler was replaced app.15-18 yrs. ago and never had any problems before.0 -
No, just remove
the vacuum disc at the outlet. It's usually in a small cage that screws into the air eliminator's body.
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0 -
Steamhead's reply
so, just remove the disc's from the vent at the top of the eliminator.can i remove the whole vent at top and replace with anormal air vent that will shut off when the steam hits it and then open later to prevent the vaccumn?0 -
Yes you can
I recommend the Gorton #2 vent as a replacement.
www.gorton-valves.com
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0 -
the final word.
to steamhead, and maddog,
thanks guys for your help. i rebuilt the old dunham air eliminator, replaced the old disc type vent w/a new gorton #2 air vent , and all seems right in the world. just returned from customers house after checking the heating system, and found his h/w heater leaking. no rest for the weary.0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements