taco 008 pump
RoosterBoy
Member Posts: 459
we may have over sized the pump on our baseboard install they will be back monday to wire and finsh up but i have 45 feet of base board that we installed
the total loop with baseboards is 156 feet they used a taco 008 will this be ok or will i have to much heat or any problems?
thanks
thanks
I do not have a B&G system syzer here, but if you go to the B&G website they have an online system sizer wheel you can plug numbers into. This should answer your question about pump size....
Good luck.0 -
007
The 007 would of worked to.0 -
thats a lot of baseboard for 1 zone !
I imagine the Delta-T's will be extremely high regardless of pump choice.
EIN
99% chance the 007 would be fine. 008 may cause noise issues with the high head.
shouldn't the guy that did it
be able answer that? Doesn't he do all of the cumberland farms and school district?0 -
siggy can make it easy
flo rate=6.6..........delta T 8.7........speed 4.1 fps.....output=26000.
merry christmas wallies!!!!
do you mean i will have noise comeing from the baseboards
but over all it will work right? and what is delta t's
my buderus is set to run at 190 deg water
thanks0 -
hi bill i did not ask him because it was his installers that was puting it in id have to waite till monday to call the office and ask him maby they did not have a 007 on the truck so they used a 008
thanks
- 119 Chimneys & Flues
- 114 Geothermal
- 165 Indoor-Air Quality
- 76 Pipe Deterioration
- 15.6K Strictly Steam
