Welcome! Here are the website rules, as well as some tips for using this forum.
Need to contact us? Visit https://heatinghelp.com/contact-us/.
Click here to Find a Contractor in your area.
looking for advise
jim murtaugh
Member Posts: 72
i service a 30 unit building w/1 apt. that becomes air bound always i suspect i have a pin hole leak in one of the garden apts. the boiler has two 2 1/2 supply and return mains and a old steel expansion tank. is there some sort of spirovent or air elimination devise i can just install on the 1/2 inch cold water supply line or do i have to split the mains and install 2 seprate devices? this apt air binds about every other week. thanks in advance and happy holidays. jim murtaugh
0
Comments
-
Hey could you fit a float style vent on the loop in question? Also, does the old ceiling expansion tank have an air-trol fitting? I think Spirovent only makes air eliminators up to 2".. after that you cani go with a spirotherm or vortec air seperator (Flanged rather than ips)0
This discussion has been closed.
Categories
- All Categories
- 86.6K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 54 Biomass
- 423 Carbon Monoxide Awareness
- 98 Chimneys & Flues
- 2K Domestic Hot Water
- 5.5K Gas Heating
- 101 Geothermal
- 157 Indoor-Air Quality
- 3.5K Oil Heating
- 66 Pipe Deterioration
- 931 Plumbing
- 6.2K Radiant Heating
- 384 Solar
- 15.2K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 43 Industry Classes
- 48 Job Opportunities
- 17 Recall Announcements