control wiring

Andre
Andre Member Posts: 11
When converting a boiler from a tankless water coil to a indirect water heater, is there any modification needed to be made to a L8124A relay before adding a three zone SR503 switching relay. Not using a cold start


Could someone give a clear explination how the high and low limit settings work? Exactly when each one does its function and whats going on to activate them.
Andre

Comments

  • Joe Mattiello
    Joe Mattiello Member Posts: 732
    Use the cold start boiler diagram

    No, just use the low voltage TT terminals on the aquastat to energize the boiler, as opposed to the ZC, ZR terminals.