Circulator won't turn on for one zone???

Adam E
Adam E Member Posts: 43
I've got a 3 zone monoflo system with one Taco 007 that's not behaving..

In the morning when I turn the t-stat up, it takes at least 10-15 minutes for the burner to kick on and the radiators (BaseRay) very slowly heat up. The other two zones seem to be fine.

Now, I'm no expert, but it seems to me that the circulator isn't on and it's heating up from gravity.

Does this sound like a bad Honeywell zone valve (V8043F1036 with terminals)?

Is the pump fired with a contact closure? If so, can I jumper two of the terminals to see if it fires the pump? I take it this would be the end switch terminals?

Also, What's up with the three other wires going to TH, TR, and THTR. I would expect only two to supply the 24v.

I'm prolly way off base here so be kind.

Thanks.

Comments

  • jim lockard
    jim lockard Member Posts: 1,059
    Yea

    Adam-- With kindness perhaps it would be best for you to consult a pro. Best Wishes J,Lockard
  • Weezbo
    Weezbo Member Posts: 6,232
    manually open that zone valve.

    if it gets hottern blue blazes then dont put your hand on it again:)
  • Paul Mitchell_2
    Paul Mitchell_2 Member Posts: 184
    That Zone

    If thtat zone heats up when the other two are on then it could be the end switch in the valve. If it doesnt matter then it could be the valve itself...but that does not happen often. also make sure there is no air in the radiators or baseboard.
  • Adam E
    Adam E Member Posts: 43


    Jim, I understand your concerns. I was just hoping that if I could isolate the valve as the problem, I could easily swap it out myself.

    Thanks.
  • Is one Taco 007

    controlling the 3 zones ? It sounds like the end switch for the problem zone isn't turning the circulator on .

    Try turning off the other 2 zones and keep the problem zone up . See if the zone valve opens , and if the circulator turns on .
  • Adam E
    Adam E Member Posts: 43


    Yea Paul, if another zones calls for heat while that first one is on, then the pump turns on and everything heats up nice.

    If it is an end switch, does that mean a whole new valve?
  • jim lockard
    jim lockard Member Posts: 1,059
    ok

    If you wish to try good luck. J.Lockard
  • Adam E
    Adam E Member Posts: 43


    Ron, yes - one Taco for three zones.

    When the other two zones are off, the problem valve opens with no pump action and very slowly heats the radiators.

    Thanks.
  • Paul Mitchell_2
    Paul Mitchell_2 Member Posts: 184
    Valve

    Depending on the age of the zonevalve you can probably just change the powerhead assembly...without draining any water. I would rcommend you call a pro though.
  • Joe Mattiello
    Joe Mattiello Member Posts: 727
    Pump is not always at fault

    If you have 1 007 circulator, 3 zone valves, and only 1 zone is taking approximately 15 minutes to energize the boiler, then the problem clearly is the zonevalve, and not the good old faithful 007 circulating pump. The zonevalve may be stuck in the open position, and allowing flow through, when another zone is calling for heat. Hopefully, you have Taco 570 series zonevalves on your system so you can replace the actuator only, and not have to drain the system, or spend more money then you need too.

    Taco, Inc.
    Joe Mattiello
    Technical Service Technician
    joemat@taco-hvac.com
    401-942-8000 X 484
    www.taco-hvac.com
    Joe Mattiello
    N. E. Regional Manger, Commercial Products
    Taco Comfort Solutions