Viessman VitoGas 100-29 Shutting down
jim_51
Member Posts: 69
Folks
I have a Viessman VitoGas 100-29 Propane boiler. It has been very cold. Range of -23 to +20. The last few days I have found the unit shut down and and the auto flue damper open. I just power down and up and unit runs fine. Baseboard copper fin throughout house. 3 zones one for Vitocell 100 DHW and other two for heat zones. Heat Curve set at 1.4 Right now the boiler is heating water to about 165. Any suggestions.
Happy Holidays to you and your families.
I have a Viessman VitoGas 100-29 Propane boiler. It has been very cold. Range of -23 to +20. The last few days I have found the unit shut down and and the auto flue damper open. I just power down and up and unit runs fine. Baseboard copper fin throughout house. 3 zones one for Vitocell 100 DHW and other two for heat zones. Heat Curve set at 1.4 Right now the boiler is heating water to about 165. Any suggestions.
Happy Holidays to you and your families.
0
Comments
-
Any Fault codes?
Are you using the Vitotronic 200? If so, any fault codes? Rebooting the computer may clear the fault, but I'd call Viessmann tech services on Monday and have them run some diagnostics over the phone.
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"0 -
Thanks Paul
Yes I do have the vito 200 control. It is not showing any fault codes.
0 -
Damper
Have you run through the diagnostic scan? Make sure the damper opens and closes during the scan. I've seen bad damper motors/end switch.
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"0 -
Sounds like
It could be a wiring problem (highly unlikely on a Viessmann) or you may have a bad vent damper that is failing to close when the burner is off. I think that there is a manual overide switch on the damper motor. This could be set to maintain the damper in an open position constantly. If the boiler doesn't lock out when you do this, you've isolated your problem.0 -
no gas?
That boiler does not like low gas pressure at all. Up here in N.E. where our natural gas supply is very limited we have issues with them going out like that. maybe withyour extreeem cold your sucking it out of your propane tank tooo quickly and it can"t boil off?
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"0 -
vitogas100
Jim
The Vitogas is very sensitive to high gas pressures if your field installed regs allow any excess pressure through when the boiler gas control closes, the vitogas control will lockout. Check the gas pressure on the boiler as it is firing and watch when the boiler gas valve closes if you get a jump in your gas pres. the next time the boiler attempts to fire it will lockout. Essentially what I am trying to explain is you are possibly getting a gas hammer(water hammer in plumbers terms)
Hope this helps0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements