EDR question
John Shea
Member Posts: 247
how to correctly size a boiler based on piping, radiators, etc.
However, how do you determine how much EDR you need to heat a certain size room?
Is there a EDR/sq.ft. rating?
However, how do you determine how much EDR you need to heat a certain size room?
Is there a EDR/sq.ft. rating?
0
Comments
-
> how to correctly size a boiler based on piping,
> radiators, etc.
>
> However, how do you determine
> how much EDR you need to heat a certain size
> room?
>
> Is there a EDR/sq.ft. rating?
Retired and loving it.0 -
John
The output of a "Square Foot" of radiation varies with water temperature. Based on the usual standard of 180°F the output of a square foot of radiation would be equal to 170 btu/square foot of radiation. Based on 215°F water or steam conditions, the output would be 240 btu/square foot. Also, Square Feet of Radiation and EDR are basicly the same thing, just different names. EDR stands for "Equivalent Direct Radiation" and more often than not is used to rate devices such as Convectors and Unit Heaters.
Glenn Stanton
Manager of Training
Burnham Hydronics
www.burnham.com0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements