hi I have a 2 ton air handler with a heating coil the loop is piped in 3/4 inch copper the loop run is 31 feet to the coil and 31 feet back to the boiler do you think a taco 007 is big enough to handle that size loop with the 2 ton heating coil or should i use a 008
thanks
thanks
Taco 007 will work
The Taco, 007 will do a nice job for you. 1 ton is equal to 12,000 btus. You have a 2 ton unit equaling 24,000 btus divided by 10,000 equals 2.4 gpm required to satisfy the load. 2.4 gpm through 31 feet + 50% for elbows and valves gives you a minimal pressure drop.
Taco, Inc.
Joe Mattiello
Technical Service Technician
joemat@taco-hvac.com
401-942-8000 X 484
www.taco-hvac.comJoe Mattiello