How to trouble shoot zone valve problem

Al_18
Al_18 Member Posts: 17
2 zone hot water system with baseboards ,first floor zone will demand heat but system doesn't respond. If I go down and hit the zone valve,the system fires up and all's well. I measured voltage on the 24v DC zone valve,it's OK. Can the zone valve stick,is that possible ? I plan to replace the valve,does that sound right?
Thanks
Al

Comments

  • Mark Walnicki_2
    Mark Walnicki_2 Member Posts: 32
    What kind of zone valve?

    My guess is the zone valve has actually opened, and it's the end switch that needs that little extra persusion to "make" and signal the boiler/circulator.

    For the heck of it, before you replace anything, I would check and double-check all your low voltage wiring. Are all connections tight? I've seen connections that *look* okay, but are barely hanging on by a thread! That could cause the problem you describe, as well.
  • curiousity kills
    curiousity kills Member Posts: 118
    zone valve

    DC?????It should be 24 vlt ac.is this a 3 wire taco? If so test on a call for heat for 24 vlt at term 1 and 2.If you have voltage there and the zone doesnt run the tsat is good but the head is not. Then try jumpering 2 and 3 and the zone should run but the head still is no good
  • jim lockard
    jim lockard Member Posts: 1,059
    in the zone

    yes sure zone valves can stick. Al depending on brand they sell rebuild kits for zone valves.
    Are all electrical connections clean and tight ? should be 24 volts AC, you can connect 24 volt light bulbs across the contacts to show when voltage is being applied. BEst Wishes J.Lockard
  • Some Auto Mag zone valves

    are DC voltage and they do stick. Is that what you have? Let us know what make you have and we can help you.
  • Al_18
    Al_18 Member Posts: 17
    Electro Zone 24v dc

    the system is 30 years old,probably needs to be replaced

  • Al, I will look that one

    up tomorrow as I do not have the zone valve book handy here at this location. I will post what I can find if anything.
  • Well how about that

    I found it in my old zone valve book. That is an old one. I can e-mail you the little bit of info I have on them just e-mail me at gastc@cox.net.

    The Models I have limited info on are the RB-4 and RB-6 which uses a 60 VA transformer with a built in rectifier to convert to 20 volts DC. It looks like when the thermostat calls it just powers the zone valve which opens. At the same time it closes a switching relay in the Electro Zone Box. the zone valve does not have an end switch.
  • Al_18
    Al_18 Member Posts: 17
    YES...that's it

    the relay kicks in and starts the circulating pump....sometimes I have to hit the zone valve to get the system to operate..I plan to replace the valve
  • Al_18
    Al_18 Member Posts: 17
    Thanks for your help

    Thanks to all for taking the time to help me out
    Al


  • ElectroZone was used alot on Hydrotherm millivolt gas boilers near thirty years ago . Here on Long Island we still see them in some areas.
    Be aware not to replace the existing 24v DC zone valve with a 24v AC zone valve unless you plan on replacing the entire controller as well. The ElectroZone controller converted ac to dc for zone valve operation by means of a 60 VA transformer and rectifier .The 24v DC zone valves did not have end switches . We have found that most problems occured because of dirty contacts on the controller.

    We on Long Island discuss this in our local BOCES (for our students), because we still have them in operation on our lovely Island .

    Hope this helps you .
    Ken Resnick

    L.A. Wilson Technological Center
    Western Suffolk Boces

    heattech@optonline.net

    There was an error rendering this rich post.

  • Al_18
    Al_18 Member Posts: 17
    Thanks to All

    Replaced the coil in the zone valave,existing coil was burnt to a crisp. Thanks again for all your help
    Al
  • Joe Mattiello
    Joe Mattiello Member Posts: 720
    Taco, 570 series

    You never mentioned the manufacturer of the valve, but if it's a Taco, you might find the troubleshooting guide I attached useful.