How to trouble shoot zone valve problem
Al_18
Member Posts: 17
2 zone hot water system with baseboards ,first floor zone will demand heat but system doesn't respond. If I go down and hit the zone valve,the system fires up and all's well. I measured voltage on the 24v DC zone valve,it's OK. Can the zone valve stick,is that possible ? I plan to replace the valve,does that sound right?
Thanks
Al
Thanks
Al
0
Comments
-
What kind of zone valve?
My guess is the zone valve has actually opened, and it's the end switch that needs that little extra persusion to "make" and signal the boiler/circulator.
For the heck of it, before you replace anything, I would check and double-check all your low voltage wiring. Are all connections tight? I've seen connections that *look* okay, but are barely hanging on by a thread! That could cause the problem you describe, as well.0 -
zone valve
DC?????It should be 24 vlt ac.is this a 3 wire taco? If so test on a call for heat for 24 vlt at term 1 and 2.If you have voltage there and the zone doesnt run the tsat is good but the head is not. Then try jumpering 2 and 3 and the zone should run but the head still is no good0 -
in the zone
yes sure zone valves can stick. Al depending on brand they sell rebuild kits for zone valves.
Are all electrical connections clean and tight ? should be 24 volts AC, you can connect 24 volt light bulbs across the contacts to show when voltage is being applied. BEst Wishes J.Lockard0 -
Some Auto Mag zone valves
are DC voltage and they do stick. Is that what you have? Let us know what make you have and we can help you.0 -
Electro Zone 24v dc
the system is 30 years old,probably needs to be replaced
0 -
Al, I will look that one
up tomorrow as I do not have the zone valve book handy here at this location. I will post what I can find if anything.0 -
Well how about that
I found it in my old zone valve book. That is an old one. I can e-mail you the little bit of info I have on them just e-mail me at gastc@cox.net.
The Models I have limited info on are the RB-4 and RB-6 which uses a 60 VA transformer with a built in rectifier to convert to 20 volts DC. It looks like when the thermostat calls it just powers the zone valve which opens. At the same time it closes a switching relay in the Electro Zone Box. the zone valve does not have an end switch.0 -
YES...that's it
the relay kicks in and starts the circulating pump....sometimes I have to hit the zone valve to get the system to operate..I plan to replace the valve0 -
Thanks for your help
Thanks to all for taking the time to help me out
Al0 -
ElectroZone was used alot on Hydrotherm millivolt gas boilers near thirty years ago . Here on Long Island we still see them in some areas.
Be aware not to replace the existing 24v DC zone valve with a 24v AC zone valve unless you plan on replacing the entire controller as well. The ElectroZone controller converted ac to dc for zone valve operation by means of a 60 VA transformer and rectifier .The 24v DC zone valves did not have end switches . We have found that most problems occured because of dirty contacts on the controller.
We on Long Island discuss this in our local BOCES (for our students), because we still have them in operation on our lovely Island .
Hope this helps you .
Ken Resnick
L.A. Wilson Technological Center
Western Suffolk Boces
heattech@optonline.netThere was an error rendering this rich post.
0 -
Thanks to All
Replaced the coil in the zone valave,existing coil was burnt to a crisp. Thanks again for all your help
Al0 -
Taco, 570 series
You never mentioned the manufacturer of the valve, but if it's a Taco, you might find the troubleshooting guide I attached useful.
Taco, Inc.
Joe Mattiello
Technical Service Technician
joemat@taco-hvac.com
401-942-8000 X 484
www.taco-hvac.comJoe Mattiello
N. E. Regional Manger, Commercial Products
Taco Comfort Solutions0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 64 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements