Question for Steamhead
gehring_3
Member Posts: 74
When measuring steam mains for the purpose of determining proper main vent sizing do you count the volume in the dry returns as well?
0
Comments
-
Just
the air in the mains, unless the vents are on the dry returns.
If this is a Vapor system rather than a 1-pipe system, the steam mains and dry returns are vented as separate units.
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0 -
Thanks Steamhead0 -
Steamhead
Do you have a direct mail addie I can contact you through?0 -
steam verses hot water
Does it save money to convert from a central heating plant to satillite {sp} boilers in all the buildings a a major university.0 -
color codes
what is the propper color for #2 fuel oil lines and where can i find the mass reg?0 -
Check your e-mail
I just sent my e-mail address to you.
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0 -
Hmmmmm
not sure on that one. I'm in Baltimore. Anyone from Massachusetts want to pick this one up?
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0 -
That depends
on a number of factors. How is the system set up now?
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0
This discussion has been closed.
Categories
- All Categories
- 86.6K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 54 Biomass
- 423 Carbon Monoxide Awareness
- 98 Chimneys & Flues
- 2K Domestic Hot Water
- 5.5K Gas Heating
- 101 Geothermal
- 157 Indoor-Air Quality
- 3.5K Oil Heating
- 66 Pipe Deterioration
- 931 Plumbing
- 6.2K Radiant Heating
- 384 Solar
- 15.2K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 43 Industry Classes
- 48 Job Opportunities
- 17 Recall Announcements