Corroded LWCO
Bill Campbell
Member Posts: 3
We replaced an older oil fired boiler w/ WM GV-3 onto a copper baseboard system. The main in the basement is black pipe, mono-flo set up. We installed a hydrolevel 1100 LWCO in the return riser. Two weeks after install, there was water dripping from the electronics of the LWCO. After removal, the probe had a lot of "crud" build up, which I rubbed off. The probe is pitted with many tiny holes. Electrolysis at it's finest. Why? What's happening in this system? What should we be looking at?
0
Comments
-
Could it be stray voltage?
Is the piping system in the home being used as a ground somewhere upstream from the LWCO? Stray currents don't have to be strong to do a real number on components. I'd try two things:
1) Look "downstream" for grounds and attach them to the incoming copper water pipe, or better yet, to a dedicated ground rod outside.
2) Electrically jumper the replacement LWCO. If the LWCO still fails in the future, you can discount the stray current theory. A bare ground wire attached to the pipe above and below the LWCO should do the trick.0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements