Steam Boiler Install Pics
Gordo
Member Posts: 857
Here is a picture of a small steam boiler that we installed this week (IN-5). This is on a two pipe radiator valve oriface system. The second picture is of an interesting tee on the dry return. The third picture is of the boiler (IN-7) that we replaced. It only lasted 10 years. The customer is very pleased with the new intallation. It's easy to do good work for good people.
with piping....
like that, I can see why it only lasted 10 yrs...what a botch job. Is that a 1 1/4" copper steam header? kpc
copper \"header\"
It was 1 1/2" copperAll Steamed Up, Inc.
https://heatinghelp.com/find-a-contractor/detail/all-steamed-up-inc0 -
Looks good!
What a difference from the "before" pics- that IN5 will last a long time and you'll have a nice warm customer.
For those who've never seen one, the special tee on the dry return is there to separate air from condensate. The Bi-Loop orifice system I worked on some years ago had one too.
Gordo, did you get any pics of the radiator valves or see who made them?
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"All Steamed Up, Inc.
Consulting0 -
Teflon tape
I never used teflon tape on a steam job. How does it hold up?0 -
for the kind words. Yes, I got a picture of the valve, but it's a bit blurry. The logo on the valve is shaped like a football with the letter "B".All Steamed Up, Inc.
> warm customer.
> too.
> _A
> HREF="http://www.heatinghelp.com/getListed.cfm?id=
> 157&Step=30"_To Learn More About This
> "Find A Professional"_/A_
for the kind words. The picture I took was a bit blurry. The logo on the valve was shaped like a football with the letter "L" inside.All Steamed Up, Inc.
It seems
to hold up quite well, with the added advantage that the joint can be un-threaded even years afterward. At least, that's what I've experienced.All Steamed Up, Inc.
Gordo - Just wondering what the cause of failure was on the old boiler after only 10 years... Seeing that header, I would assume the heat exchanger cracked due to the unit running almost continuously or something.... Nice work on the new one and good point about being able to unthread the joints years later with teflon tape... I always try to plan on easy maint. years down the road...0 -
copper on steam ok, but only, if
"K" thickness, silver brazed, and refigeration grade fitings, and lots of insulation0 -
Thank you for your comments! The old boiler failed
sometime last year and I believe the cause was too much make-up water. Most of the two pipe radiators had Hoffman #40 steam vents on them and one radiator had an open hole (since plugged). That radiator is also piped so that the cut-off valve is on the outlet side. This is to be corrected. The main vent on the separator tee was from the coal era (vacuum) and the check was found to be shut. I think it was shut because steam from the main was piped directly over to the dry return drip (see "before" picture), and hence that's why the Hoffmans were "needed" to get the radiators hot.All Steamed Up, Inc.
I've seen that logo
but can't remember the name it stands for. I know I have it in one of my old books, if I find it I'll post it here.
Consulting0 -
Kal
Due to things we see out in the field that seem to be related to the use of copper on the steam carrying pipes, we have addressed the use of it in the I&O manual for our steam boilers. It is OK if used on the wet returns only. Thanks.
Glenn Stanton
Manager of Training
Burnham Hydronics
www.burnham.com0 -
Oh, and the customer said
that the copper "header" leaked a bit, too.All Steamed Up, Inc.
Another one joins the Drop Header Club
Great work Gordo . I like the full sized equalizer piping . And we use Teflon also , for the same reason . Holds up very well over a long time .0 -
Thanks! I'd been dying to try
> time .
a drop header ever since I saw it on this site. Then I got a copy of Alt's Domestic Heating Plans (a DeadMan book) and saw it there, too. And with the low headroom in this particular installation, I couldn't resist. The drop header and the full sized equalizer makes for a steady water line, even with dirty water (even so, this boiler was cleaned, of course ).All Steamed Up, Inc.
- 86.7K THE MAIN WALL
- 56 Biomass
- 104 Chimneys & Flues
- 5.6K Gas Heating
- 103 Geothermal
- 159 Indoor-Air Quality
- 69 Pipe Deterioration
- 942 Plumbing
- 6.2K Radiant Heating
- 385 Solar
- 15.3K Strictly Steam
- 43 Industry Classes