Venting one pipe steam system
MattV
Member Posts: 27
I have a one pipe steam system. In Dans book he says to vent the larger rads quicker than the small ones not by where they are in your home. How do you know how fast to vent them? Do you vent them according to where they are in you house as well as the size of them? Hope this makes sense.
0
Comments
-
venting
It mostly trial and error. It's a balancing act. You have to "tweek and twiddle" until you get it right. If the room overheats, close the vent down (slower venting), if the room is cool, open the vent more (faster venting). It doesn't get much more scientific than that.
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"0 -
Just as important as radiator vents
are the vents at the ends of your steam mains. These have a profound effect on system performance. They must be large enough to vent all the air in the mains in about a minute, measured from the time the boiler starts making steam. Then all the radiator vents have to do is vent the radiators and the piping connecting the radiators to the mains.
Measure the length and diameter of your steam mains and tell us what vents are on them. We can tell you what you need.
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0 -
mains
I have 2 mains one measures about 34 1/2 qand the other about 37 1/2. I use ventrite 35 on both mains. You had told me a while ago to use 2 vents on each main. The problem is I can't find a plumber who wants to do the job. They keep telling me it is not neccesary. I suppose I will keep looking in the mean time what should I do?0 -
No plumber wants to be bothered with my little job
No disrespect to the true professionals who lurk on this site. Do you wonder why some of us flock to the big box stores and and join the DYI movement??0 -
this is what I have done...
with materials from the dumpo (home depot). Of course you will have to find a place to get the main vents.0 -
TRVs
Hello Matt:
You could also install 1 Pipe Steam Valves, Thermostatic Operator and a vent to each rad so that your room does not overheat.
Check the Library on this site under Thermotatic Radiator Vavles for more details. Althought the part numbers have changed, the product is still available.
Warm Regards,
bb0 -
pipe connection with teflon ?
I have been pondering how to add multiple main vents - (thanks to Steamhead for starting me looking at this). Q: what did you use to seal the pipes at the threads - I see the teflon ... is this sufficent to make it air tight on the connection of this size ?0 -
question for Steamhead
Do I need more than 2 Gorton #2s and a Hoffman #75 to vent 90' of 2.5" steam main at the proper rate?0 -
That combination
should work fine. If there are any other steam mains on that system, make sure they are properly vented also.
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0 -
one other lengthy question for Steamhead
Thanks for the info Steamhead.
I think that I am correct in my diagnosis below but want your opinion before I call the plumber in:
The steam system in question is a 2-pipe air vent system. According to "the Lost Art" the returns should be piped directly to the wet return in the basement. In my system the returns come down and connect with the drip leg from the steam riser at a point that is about 30" above the wet return and about 14" above the water line. There are also flow check valves on every return pipe that are installed to not allow anything to go 'up' the return pipe. The boiler was replaced about 4 years ago by some knucklehead and Jamie Pompetti redid all the near boiler piping for us last Feb. The issue that I am having is steam getting into the returns (causing a bit of hammer near the end of the cycle) and not necessarily getting all the way up to the rads on the second and third floors. My theory is that since the old boiler's water line was above where the returns connect to the drip leg, steam was never able to make it into the returns. Now that the water line is much lower, steam is free to get into the returns. I think that the fix is to lower that connection point to somewhere below the current water line. What is your opinion?
Another option just occured to me: will the flow checks stop air and/or steam or are they designed to work only with water? if they would work with air, maybe all I need to do is to replace the guts on them or clean them up? What do you think?
Thanks in advance,
Thad0 -
Where to buy
Where can I buy those. I have had no luck looking for them.
0 -
See the other thread
for my answer.
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0 -
where do you live?
that will help to refine the search.
bb0 -
did you try
find a pro0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 64 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements