Zero Pressure on Boiler
RSGlass
Member Posts: 4
I have an old boiler (circa 1925) that shows a zero pressure reading when it's not operated, but normal (about 15) when the thermostat is turned on. I don't think the zero pressure is due to a leak, because adding water makes the pressure skyrocket. So the water level seems to be correct, the radiators have been bled, and pressure continues to drop to zero once the thermostat switches the boiler off. What's theh problem?
0
Comments
-
The expansion tank
is "flooded" and lost its capacity to maintain system pressure in the typical range of 12 # cold - 20 # hot.
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"0 -
expansion tank flooded fix
What's the fix when the expansion tank is "flooded"? Is this easy to correct?0 -
Is it the old plain tank? They're usually painted black or silver, quite long and are hanging between a couple of floor joists near the boiler.
The other type is more modern, frequently gray (you might have more than one on a big old system) and you'll see an air fitting (like a tire) on one side.
Which do you have?0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements