flow control's?
[Deleted User]
Posts: 0
hey all, few questions here.. on a hw system(loop,diverter or gravity). if there are independent zones with pumps and zone valves for each one, is there a need for a flow control? usually, people install them above the zone valve which i can't understand.. once the zone valve closes on the feed side, water will not pass through into the boiler to lose heat? where would a flow check be needed? also, how far of a run can a 007 run on? thanks all.. happy holiday's.. mike
0
Comments
-
zone valves for flow control
Using zonevalves for zone control is a nice alternative to flo-checks. Flo-checks prevent migration of hot water in one direction, which does not guarantee induced flow. Using a zone valve will positively stop flow in either direction making that a superior alternative. The Taco 007 will handle a 100,000 BTU boiler with no problem. As for the maximum length of pipe, that is a variable. However, you should be fine with lengths up to approximately 200 lineal ft.
Taco, Inc.
Joe Mattiello
Technical Service Technician
joemat@taco-hvac.com
401-942-8000 X 484
www.taco-hvac.comJoe Mattiello
N. E. Regional Manger, Commercial Products
Taco Comfort Solutions0
This discussion has been closed.
Categories
- All Categories
- 86.6K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 54 Biomass
- 423 Carbon Monoxide Awareness
- 98 Chimneys & Flues
- 2K Domestic Hot Water
- 5.5K Gas Heating
- 101 Geothermal
- 157 Indoor-Air Quality
- 3.5K Oil Heating
- 66 Pipe Deterioration
- 931 Plumbing
- 6.2K Radiant Heating
- 384 Solar
- 15.2K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 43 Industry Classes
- 48 Job Opportunities
- 17 Recall Announcements