Panel photo ( milne)
ScottMP
Member Posts: 5,883
a job that Steve had been doing. You guys saw the boiler photos of the two Viessmans.
This is for the radiant floor in the master bath and a Unico coil ( installed by others ) that sits in a cold attic location so we antifreezed it.
Scott
<A HREF="http://www.heatinghelp.com/getListed.cfm?id=237&Step=30">To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"</A>
This is for the radiant floor in the master bath and a Unico coil ( installed by others ) that sits in a cold attic location so we antifreezed it.
Scott
<A HREF="http://www.heatinghelp.com/getListed.cfm?id=237&Step=30">To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"</A>
0
Comments
-
A wonderful...............
way to send heat through a fan coil.My only ? is won't the Buderus mixing station and the Viesmann boilers quarrel at the least..............or even worse!!!???!!!!
Nice mounting up Christopher.BTW Mr Scott.......where did you stay in the park........still wearing your ears:)
cheese0 -
Viessmann and Buderus
Each have there own Tekmar and sense the water temp so fighting should be kept to a minimum.
We stayed at the Wilderness Lodge. A huge place witha great pool
No Ears for me Just the green bottle.
Scott
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"0 -
Nuttn'
like the Magic Kingdom!Our crew spent quite sometimes there...........talk about memories!
cheese
PS.........Off to a crawl now...........water pressure problem and its 20° outside.MOOOOOOOMMMMMMMYYYYYYYYYY!!!!!(reality)0 -
Candy for the eyes
Nicely done!
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"0 -
You mean
The panel right ?
You had me worried.
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"0 -
Is this home
built into a mountain ? Steve does great work . What material is the wall panel made of ? Looks like sheet aluminum ?0 -
Plywood
with silver paint
I can't afford that diamaond plate stuff
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"0 -
just a reminder from a siggi artical ...
make sure the controls interlock so that the primary system is on and up to temp before turning on the secondary pump with the antifreeze loop - because with only a cupful of water in the FPHX, 20 degree antifreeze water pumping through the secondary can very quickly freeze and bust the cupful of water on the primary side of the hx - worse it will fail internally by moving the plates enough to uncover the alternating holes and expose the systems to each other - thereby diluting the antifreeze into uselessness - and then you'd have a real problem
a good old fashioned high-voltage clamp-on aquastat should do nicely for this0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements