Water level in glass gage ?? help?
Todd Proia
Member Posts: 3
Help,, I just had to put in a new steam boiler after one had cracked. And what is happening is that when cold the water level in the glass is a little above halfway, after firing for a little bit (15min) the water is very low in the glass gauge. I turn off the boiler and immediatly the water line in the glass gauge goes back up to the middle minus the condensate.. any idea why? Is this bad? Thanks in advance
0
Comments
-
Might be
the water under steam pressure pushing out of the boiler through the return piping . Would you know if they installed an equalizing pipe with a Hartford Loop ? The pipe size is critical too . And what brand boiler is it ?
If the water level rises back up immediately after shutdown then I wouldn't think it's clogged returns . But it is a possibility .0 -
Todd....
Can you post a picture of the boiler/near boiler piping. If I had to make a guess (without more info, its just that) I'd say the boiler might be surging. If the boiler is surging, then it will have to be skimed...Read the installation instructions on skiming....Robert O'Connor/NJ0 -
Water Level
You may have some surging going on due to oils that have accumulated on the water surface from the installation of boiler, pipe and fittings. But the true fact is that the gauge glass sometimes is really not indicator of the acual water level in the boiler. The reason for this is that when the water in the boiler begins to boil, the steam bubbles rising through the boiler water will displace the water and actually make the water level rise instead of what you are seeing in the gauge glass. When you shut it down the water stops boiling and the level reurns to normal levels. Here is a graphic from GAMA - IBR Hydronics Institute that represents that very well. Hope this helps.
Glenn Stanton
Manager of Training
Burnham Hydronics
www.burnham.com0 -
it is a burnham inv-6-1 the pressuretrol is set at 1.5 and the dif at a little over 1? also pic is posted0 -
Thank you for the explanation. I was starting to get worried , didn't want it to dry fire or anything.. thanks
0 -
The header and return piping
look great , and sized right . Robert and Glenn got it right .0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements