WILL THIS WORK? SYSTEM PIPING

DAVE_48
DAVE_48 Member Posts: 2
Will this system work? It has 3 zones of baseboard and 2 zones of low temp radiant, all pumps have check valves. Any comments?

Comments

  • Mike Kraft_2
    Mike Kraft_2 Member Posts: 398
    loads?

    Don't know what boiler or controls you are proposing. But a primary/secondary stradegy may help this schematic.Some boiler/and condensate protection.

    cheese

    PS (typed in after my above post)
    Boy do I feel like a dumb ****............just walked in looked and didnt see!.................Very nice drawing:)I really like the primary /secondary.A very nice touch.Sorry about that!
  • hr
    hr Member Posts: 6,106
    You may

    in fact you probably will, need flow checks or protection on the returns also. Especially if they are taken off the top of the primary loop like that.

    The three way may offer enough resistence to provide flow check with just a check pump on the supply side.

    Checks are cheap and always easier to install on the first go around.

    I'd rather not see the two pumps on the mixer taken off a bullheaded tee like that. Run a straight piece of copper and branch off the sides.

    hot rod

    To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"
  • A.J.
    A.J. Member Posts: 257
    Dave group your supply

    and returns together otherwise you will not be able to supply your design temp.at the zones down stream.
    Looks good otherwise.

    A.J.