WANTED USED HOFFMAN DIFFERENTIAL LOOP

Where would you search to find a used Hoffman Differential Loop (No. 1) to replace a cracked one.

Can the old one be repaired by welding it?

Thank you for you help.... Rick

Comments

  • Joe C
    Joe C Member Posts: 10
    Diff loop

    What size do you need?
  • gerry gill
    gerry gill Member Posts: 3,078
    why?

    why do you still need it? does your boiler run on coal?
    gwgillplumbingandheating.com
    Serving Cleveland's eastern suburbs from Cleveland Heights down to Cuyahoga Falls.

  • Rick Salvador
    Rick Salvador Member Posts: 5


    The model is NO. 1. The building is around 2,000 square feet. My boiler was replaced and we found that the loop was cracked. We tried installing a Hartford loop but the water surges from the bottom of the glass to the top. This did not happen while the Hoffman loop was attached.

    Thanks, Rick
  • Rick Salvador
    Rick Salvador Member Posts: 5


    Our new boiler ran fine until we removed the Hoffman Loop. We have added the Hartford loop but there probably has to be more changes done to stop the boiler from surging.
  • Steamhead
    Steamhead Member Posts: 17,539
    Rick, a Hoffman Vapor System like yours

    will run fine without the Differential Loop. The Loop was there to make sure the water could get back to the boiler if the pressure got too high. Nowadays we use a Vaporstat to limit the boiler's pressure to less than 1 pound.

    There are two caveats to removing the Loop. 1- Do not replace it with a straight piece of pipe between the steam main and the dry (overhead) return. This will pressurize the return so steam will not flow.

    2- Make sure the dry return is well vented. The vent in the top of the Loop was the only vent in the system. Use at least one Gorton #2 vent on the dry return, and if there's more than one dry return they all need either individual vents or access to a central vent. If the air can't move from the radiators into the dry return and out the vent, the system won't heat properly and the boiler may surge.

    If you're not sure of the piping configuration, post some pics here and we'll see what we can do.

    To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"
    All Steamed Up, Inc.
    Towson, MD, USA
    Steam, Vapor & Hot-Water Heating Specialists
    Oil & Gas Burner Service
    Consulting
  • Rick Salvador
    Rick Salvador Member Posts: 5


    Gerry,

    Here are a few pictures of how the system is connected now.
  • Steamhead
    Steamhead Member Posts: 17,539
    Near-Boiler Piping is Wrong

    We install that line of Columbia (or Utica) boilers so I can tell you it's not right. You'll find the piping diagram in the installation instructions, which the installer probably used for knee pads.

    You need a proper header- 2-1/2-inch or 3-inch on that boiler depending on its capacity- with two risers from the boiler to the header and a riser from that to the steam main. Here's a shot of a similar boiler we did- two risers to a drop header, and two steam mains leaving the header.

    Also that dry return vent looks awfully small. It's probably a Hoffman #5 or #6. If it's a #6 it's a Vacuum vent, which can do all kinds of strange things to an oil- or gas-fired system. Change it to a Gorton #2 and watch how much better the system works.

    www.gorton-valves.com

    To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"
    All Steamed Up, Inc.
    Towson, MD, USA
    Steam, Vapor & Hot-Water Heating Specialists
    Oil & Gas Burner Service
    Consulting
  • Rick Salvador
    Rick Salvador Member Posts: 5


    Gerry,
    My steam boiler is a Utica model# PEG300CIDE serial# UAB12596. It produces 182,300 BTU/HR and 760 sq. ft. of steam. There is also another BTU rating on that has it at 299,999 and a steam rating of 15 PSI.

    Thanks again, Rick
  • Steamhead
    Steamhead Member Posts: 17,539
    The PEG-300

    needs a 3-inch header. Anything smaller won't let water separate from the steam.

    BTW, my name's Frank.

    To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"
    All Steamed Up, Inc.
    Towson, MD, USA
    Steam, Vapor & Hot-Water Heating Specialists
    Oil & Gas Burner Service