Chimney Draft

Paul_28
Paul_28 Member Posts: 113
How and when is it tested?

Comments

  • Pinball
    Pinball Member Posts: 249


    It should be tested anytime the burner is cleaned and adjusted, and before and after a routine maintanence. It is done with a draft gauge inserted into the smoke pipe/vent, before the draft stabilizer and at least six inches from the breech of the boiler and over the fire, through the small hole in the inspection door of the chamber. the readings are measured in inches of water column.
    Al
  • Paul_28
    Paul_28 Member Posts: 113
    Chimnet Draft

    I have a gas boiler, no inspection door. How long should the boiler run before takeing a measurment?
  • curiousity kills
    curiousity kills Member Posts: 118
    draft

    You need to check after the draft hood.Looking for -.02 to-.04