hi co reading
ed wallace
Member Posts: 1,613
I replaced a 75 gallon gas waterheater today after turning it on i noticed back pressuere at the draft hood due to partailly plugged chimney after clearing chimney blockage the co readings went up to 200ppm when the boiler runs no problems vent for waterheater is lower then the boiler vent 1 side of the chimney is on an outside wall any suggestions other then rerouting vent so its higher then the boiler vent
<A HREF="http://www.heatinghelp.com/getListed.cfm?id=256&Step=30">To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"</A>
<A HREF="http://www.heatinghelp.com/getListed.cfm?id=256&Step=30">To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"</A>
0
Comments
-
Where are reading this at? Also what about stack temperature, draft and 02 readings? You may have an air curtain effect going on.
Brian0 -
In Mass it's code to vent your water heater before your boiler.. almost sounds like maybe the chimney liner is shot, or oversized, and when only the water heater is firing the stack can't get up to temp and causes down drafts... does the chimney ever condense?0 -
hi co
will be going back tomorrow to inspect the chmney during the day was hard to see if it was lined old waterheater had worked for 10 yrs no problem
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"0 -
huh?
It's mass code to vent below the boiler vent going into a chimney?0 -
Agree with Brian
What were your other readings AND what was the draft AFTER you cleared the blockage?
Where in the flue were you testing?
When you go back, check those things and let us know. We can fix this together!
AND MOST IMPORTANT.................THANKS FOR TESTING!!!!!!!!!
All the best my friend!
Mark H
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"0 -
Check the input rate too
it may be a bit high and only producing CO under certain draft conditions.
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0 -
high CO readings
did a test using a testo combustion effiency tester 1 st test with boiler off the readings are stack temp 506 degrees 02 6.5 eff 80.4 CO2 8.1 draft 0.00 test 2 with boiler running stack temp 520.7 02 7.0 eff 79.0 CO2 7.8 0.02 chimney is not blocked
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"0 -
high CO
anyone have any other ideas
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"0 -
Is this a gas boiler Ed?
Mark H
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"0 -
high CO readings
mark its a bradford white 75 gallon gas water heater
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"0 -
Check your e-mail Ed. (nm)
Mark H
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 64 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements