Vaporstat Settings
Fred Clough
Member Posts: 2
How do you determine proper Vaporstat settings? I just had one installed (current settings are cut in at 2oz and cut out at 6oz, I believe). There are nine rads in my system. Peerless boiler.
I was reading pg 14 of "The Lost Art of Steam Heating" and Dan indicates a cut in at 4 and cut out of 10. Should I interpret that to mean everyone who has a vaporstat should use those initial settings?
Since I'm a layperson, if I raise the cutout from 6oz to 10oz, what will this really do? Keep the boiler going longer? Burn more fuel?
Any help would be greatly appreciated as there isn't a lot of info available on the web.
Thanks in advance.
Fred Clough
I was reading pg 14 of "The Lost Art of Steam Heating" and Dan indicates a cut in at 4 and cut out of 10. Should I interpret that to mean everyone who has a vaporstat should use those initial settings?
Since I'm a layperson, if I raise the cutout from 6oz to 10oz, what will this really do? Keep the boiler going longer? Burn more fuel?
Any help would be greatly appreciated as there isn't a lot of info available on the web.
Thanks in advance.
Fred Clough
0
Comments
-
The cut-out should be
at 16 oz. and the 'DIFF' should be set at 12 oz. The Cut-out on the L408 is also called the 'Main'.
JMO, but it works 98% of the time for me with new or old boilers.0 -
Vaporstat pressures and models
I have a new Weil Mclean residential SGO boiler with a Honeywell pressurestat I can't control well. Need a Vaporstat. Any recommended models? Also, is Dan's 10 oz/4oz cutout/cutin setting right? Won't there be too much cycling of burner? At about 1.9psi/.9 psi, I'm getting 5-7 cycles in this late fall weather. Maybe I need to cut back on burner fuel rate too?0 -
It depends
Many vapor systems are not to be operated above 8 ounces because it will cause steam to enter the returns...so your high setting should not be above 8 ounces. However other vapor systems can be run higher. So it really depends! More info on what type of sytem it is will help, or better yet a site visit from a truly knowledgable steam contractor would be good.
Boilerpro0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 64 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements