Should the bypass be above or below the circulator on the supply line?
By pass
For boiler protection after the circulator , for system temperment before the circulator..0 -
In a 3 zone, 3 circulator system where would the bypass be located. Above which circulator or doesn't it make any difference?0 -
By pass
It depends, explain system and purpose of by-pass.0 -
Purpose is to prevent thermal shock to boiler
by having water that is too cool enter the system. System is a low mass cast iron Biasi with a 3.8 gal water content. System is in a split level with each level a diferent zone. Slant fin 30 baseboard installed with 4 baseboard units on each floor. Heat loss calculation of 37,663 BTU/hr using the Slant Fin program.0 -
You don't need a bypass(NM)
Instructions
Read Biasi instructions, you don't have high mass radiation .If they insist pipe it Primary Secondary piping. Dan sells a book on the subjuct.
Jed mentioned you don.t need one. I myself is not familiar with a Biasi .0 -
it would be...
overkill to install a bypass...and if you insist you would need one after each circulator. You could use zone valves for such a small system and be fine. kpc