\"additive\" or \"subtractive\" pressuretrol?

Larry Peck
Larry Peck Member Posts: 13
I own an older home with one-pipe steam heat. I understand from Dan's great book, "The Lost Art of Steam Heating," that the pressuretrol cut-in should be 1/2 psi and the cut-out should be 1 1/2. However, I do not know whether the pressuretrol is "additive" or "subtractive."

The pressuretrol is a White Rodgers, Type 1204-5, Style B-2. I do not know the age, but it is not new. Removing the metal cover plate reveals two wheels, a large lower wheeel numbered from 0 to 10 in 1/2 psi increments but having no other markings, and a small upper wheel marked "PSI Diff." My question is whether the large lower wheel is the cut-in pressure (indicating an "additive" pressuretrol) or the cut-out pressure (indicating a "subtractive" pressuretrol).

Also, how do I know if the pressuretrol even works if the pressure gauage no longer functions?

Many thanks in advance for you replies.

Comments

  • David Efflandt
    David Efflandt Member Posts: 152
    get working pressure gauge

    White Rodgers has nothing about pressure controls on their website. But since the one dial goes down to zero, I would assume that would be cut-in and differential would be additive.

    You should really get a working pressure gauge, but it is hard to find one high enough for relief setting that indicates below 2 psi, so I use a pressure/vacuum gauge. That way I can see it rise from zero and shut off before 2 psi (minimum settings on my Honeywell pressuretrol are 0.5 psi cut-in and 1 psi rise). Original gauge when I moved into home had plugged connection, so it was just reading trapped pressure instead of boiler pressure, and would not even go all the way down when removed (stuck).
  • The WR is

    additive. The MH w/ the plastic cover (L Series) is subtractive. The MH w/ the metal cover (PA Series) is additive. That is, when it works.

  • Larry Peck
    Larry Peck Member Posts: 13
    recommendation for new pressuretrol or vaporstat

    Thank you very much for your prompt and informative replies.

    Could anyone recommend a replacement pressuretrol? Should I purchase a vaporstate instead and, if so, could someone recommend a make and model number (which sits on top of the low water cutoff valve)? Does a pressuretrol make sense for an old boiler? Thanks in advance for any replies.

    Larry