One caution is to watch out for tall risers that feed TRVs with no way to vent the top of the riser into the return (crossover trap).

When a TRV shuts off at the top of a riser, the riser cools and fills with water FROM THE TOP DOWN!!!! Just like a drinking straw. When the TRV opens, there is a column of water that the steam can't lift, and that won't drop down into the main. It acts like a frozen pipe, which it would eventually become.

When you shut off the system, it cools down and the water falls back to the main.

When it runs next time, a different riser does it, but exactly the same symptoms. It'll drive you up a wall!

Crossover traps at the top of the risers cures it. It'll pay for itself in comfort and saved fuel.

Noel

Comments

  • Charlie_9
    Charlie_9 Member Posts: 4
    Thermostatic Radiator Valves

    I'm looking for advice on the wisdom of installing TRVs on my two-pipe vapor system. Can and/or should it be done? The system, installed in 1929, has Hoffman controls. Is there a TRV that can be installed directly on the original Hoffman #7 valve, or does the whole valve body assembly need to be replaced?