What's causing high pressure in HW Boiler
Kyle Kubs
Member Posts: 12
Ok, I need to defer to the real pro's here... Inspected a house last month. Older oil fired weil HW boiler. Pressure cold was around 20psi. A bit high, especially for a two story on a slab, 12 would have been fine, but ok... Crank er up and the pressure starts climbing right away. I'm watching and it hits 30... 31...32... Still no discharge from the PRV. I shut it down and check the expansion tank - the first few inches near the tapping is good and hot but the rest is cold so I assume the bladder isn't ruptured and the tank isn't water logged. So my question is, barring a bad expansion tank, what else would cause a high pressure condition like that. I did turn off the fill valve to isolate a pressure reducer that was being somehow affected by the heat even though that is unlikely. Of course I recommended the client bring in a hydronics pro for an evaluation but they never get back to me to let me know what it was...
0
Comments
-
You Told us the water pressure is 20 psi.
Theres the answer.reduce the start up pressure ,reduce the temperature, not everyone uses a 30 psi pop off...the domestic coil has a leak that gets particulairily bad with heat,the gage is lying to you,the high limit is fried and the gage is lying there by pumping X psi cold water to<Temps than normal.. theres a few ideas on what may be happening.0 -
rising pressure
It would have to be either a blocked line to expansion tank or a bad or depressurized expansion tank. Also check setting on prv, if 30 and gauge is accurate, replace it. Also agree that the pressure only needs to be around 14-15psi. Good luck, PS it could be what Weezbo say's also but I would be surprised.0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements