Split-zone options
Dave_46
Member Posts: 6
I am replacing a boiler and one zone is a split zone. The zone heats with cast-iron baseboard on a single loop system with mono-flow tees. The two branches of the zone are 1" and the lines to the radiators are 1/2" The current set up is installed incorectly with the two sides of the zone returning on one 1" line. The return line should be 1 1/2" to accomodate the flow from the two 1" lines. The return on the new boiler is 1 1/4". Can I change the return to 1 1/2" and then split it again to two 1" lines right before I go into the return manifold at the boiler? Or, should I just make it a single loop and move some of the mono-flo tees. The zone has about 60 feet of baseboard on it. Is this to much baseboard for this one zone?
0
Comments
-
If I read this right, you have a 1" supply with 1/2" feeds to the baseboards and then return on 1". If it is working, heating comfortably then why change it?0 -
what is the total load...
for the entire house? 1" can do 80,000 based on a 20* delta T. 11/4" can do 140,000...1 1/2" seems a bit overkill....kpc
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"0 -
split-zone options
The problem is that it is not heating properly now. Because the two branches of the split-zone which are 1" return to the boiler on one 1" line there is back presure on the two supply sides of the split-zone. Apparently my question was not clear. If I change the 1" return line to 1 1/2" to accomodate the flow from the two 1" supply sides of the split-zone, can I then split the 1 1/2" return line back to two 1" lines to go back into my1 1/4" boiler return manifold?0 -
The total load
The zone has about 60 feet of baseboard so the load is 34,800.0 -
split-zone options
Kevin,
Only one of the zones in the house is a split-zone. The other zones are single loops. The split-zone has about 60 feet of baseboard so the load is about 36,000 btu's. I figured 1" could handle this, but wondered why they would have split the zone when they installed the system.0 -
Where and how are the monoflo tees installed?
Is the zone above the boiler. Are the monoflo tees on the supply or the return or both?0 -
where the monoflo tees are installed
The Zone is above the boiler and the monoflo's are on the return side of the radiators.0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements