Split-zone options

Dave_46
Dave_46 Member Posts: 6
I am replacing a boiler and one zone is a split zone. The zone heats with cast-iron baseboard on a single loop system with mono-flow tees. The two branches of the zone are 1" and the lines to the radiators are 1/2" The current set up is installed incorectly with the two sides of the zone returning on one 1" line. The return line should be 1 1/2" to accomodate the flow from the two 1" lines. The return on the new boiler is 1 1/4". Can I change the return to 1 1/2" and then split it again to two 1" lines right before I go into the return manifold at the boiler? Or, should I just make it a single loop and move some of the mono-flo tees. The zone has about 60 feet of baseboard on it. Is this to much baseboard for this one zone?

Comments

  • Maine Ken
    Maine Ken Member Posts: 531


    If I read this right, you have a 1" supply with 1/2" feeds to the baseboards and then return on 1". If it is working, heating comfortably then why change it?
  • kevin coppinger_4
    kevin coppinger_4 Member Posts: 2,124
    what is the total load...

    for the entire house? 1" can do 80,000 based on a 20* delta T. 11/4" can do 140,000...1 1/2" seems a bit overkill....kpc

    To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"
  • Dave_46
    Dave_46 Member Posts: 6
    split-zone options

    The problem is that it is not heating properly now. Because the two branches of the split-zone which are 1" return to the boiler on one 1" line there is back presure on the two supply sides of the split-zone. Apparently my question was not clear. If I change the 1" return line to 1 1/2" to accomodate the flow from the two 1" supply sides of the split-zone, can I then split the 1 1/2" return line back to two 1" lines to go back into my1 1/4" boiler return manifold?
  • Dave_46
    Dave_46 Member Posts: 6
    The total load

    The zone has about 60 feet of baseboard so the load is 34,800.
  • Dave_46
    Dave_46 Member Posts: 6
    split-zone options

    Kevin,
    Only one of the zones in the house is a split-zone. The other zones are single loops. The split-zone has about 60 feet of baseboard so the load is about 36,000 btu's. I figured 1" could handle this, but wondered why they would have split the zone when they installed the system.
  • Bruce M.
    Bruce M. Member Posts: 143
    Where and how are the monoflo tees installed?

    Is the zone above the boiler. Are the monoflo tees on the supply or the return or both?
  • Dave_46
    Dave_46 Member Posts: 6
    where the monoflo tees are installed

    The Zone is above the boiler and the monoflo's are on the return side of the radiators.
This discussion has been closed.