buderus logomatic
Bluenose_21
Member Posts: 14
I'm servicing two ge615 buderus boilers with logomatic controls. My problem is that the logomatics shuts down the indirect circ before it ever reaches temp.I set it for 120, it goes to 115. If I set it for 135 it goes to 129.What's up with this? Any help would be appreciated.
0
Comments
-
Have you
Checked actual tank temp vs. what the display is reading?
Make sure the sensor is in all the way and in good contact with the well.
Is it a Buderus indirect?0 -
tank temp
The tank is a 500 gal storage with sidearm /rapfast heater.Sensor is in a dry well in the middle(end) of tank.Water from the top of tank is approx 10 degrees higher than display is reading. But doesn't the display show what the control(logomatic) thinks the tank is?0 -
Make sure
The sensor is in good contact with the well. You have to remember that the sensor is electronic not hydraulic cap tube type. If it's flopping around in an oversized well it will give false readings. Try filling the well with some heat conductive paste and see what happens. Buderus also has specs on what specific resistance the sensor should read at a given temp. If it doesn't match those you could have a faulty sensor. Also with that size of a tank you are going to get some noticeable variation of temps within the tank itself unless it is constantly circulated.0 -
The control is smarter than you think it is...
I used to get irritated at the same thing. THe boiler would shut down before its temperature reached 180 degrees, and before the tank reached it's set point. Then, I sat back and watched, and to my amazement, the tank "coasted" up to its set point. The logic can "see" rate of recovery and knows how much energy it has that can be transfered without having the flame rolling. Look a little closer and I think you'll find that the tank coasts up to its set point. No waste, just whats necessary. It also learns over time and adapts accordingly.
ME
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"0 -
Good answer Mark
always nice to know there are those that pay attention. Good Job0 -
Mark's answer
Right on the button - it's the "Fuzzy" logic of the Logamtic Control. Thanks Mark!!0 -
foggy
Is there no way to override the logic?I think that the fuzzy logic is alittle foggy.I realize that the boiler temp coasts up to its set point but the dhw never reaches temp.The only time it has reached temp is when I switched the control to manual and let rip for a few hours.If left on auto it goes to where it wants then waits for a drop in temp to start the pump again.This is a 100 unit apartment building, has a major draw from the tank first thing in the morning.It has continuous recirc. Tenants and super are not impressed with the cooler water.Tenants complain to super, super complains to me, I scratch my head,these are my first experience with the logomatic controls.These are replacement boilers, the hot water used to be control by a aquastat, in the same well, set between 130-140.0 -
Priority??
Is the DHWtank set for priority zoning? Or are the heating pumps on at the same time?
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"0 -
Blue nose
Check the thermister to make sure it is correctly reading the tank. You may have a bad sensor. Steves right , you should check the resistance.
Marks correct about the fuxxy logic, but what I here you saying is that it Never reachs the set point. Is that correct ?
Where do you have the recirc line connected ?
I would believe the control should read very close to what the real tank temp is, but where are you reading the tank temp from ? You mentioned that the tank is hotter at the top which would happen in that large a tank, due to stratification.
Are you reading the temp at an outlet faucet ? You would lose alot of temp as it travels thru the building piping.
Scott
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"0 -
WARNING! VERY IMPORTANT!!!!!!!
DO NOT EVER PUSH THE CHIMNEY SWEEP MAN BUTTON ON THE 2107 !!!!!!!!!!!
Once you awaken him - there is no stopping him.
He does not sleep.
He does not eat.
He does not rest.
He never stops looking for Sarah Connor, I mean the hydronic trash home owner.
He will rip the condemned boiler out and throw it in the street.
Your neighbors will be forced out in the street to laugh at you.
PLEASE NEVER PRESS THAT BUTTON!!!!!!!!
Darin0 -
What the heck????
I've never pushed that button, but now I want too. It's Just like telling a kid never to put beans in his ears. It probably wouldn't of occured to me to push it. Now I want to call my last Buderus install and make up an excuse to do so. Ack! Must... resist..... temptation. Good thing I'm leaving for Wetstock today. Maybe I'll forget before I come back. BTW what is that button supposed to do? WW
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"0 -
temp
Scott, It won't reach the set point.The only time it did was when I switched it to manual.The recirc is into the bottom of the tank at the opposite end from sensor.I read the temp from relief valve(thank God for floor drains).I am going to test the sensor tomorrow.But the only thing I can't get my head around is that the if the sensor/thermister is bad,where does the control get the number that is showing me(ie. DHW temp.)?Isn't it what it is sensing in the tank?0 -
kinda sounds...
like something from Dr Seuss...kpc
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"0 -
Paul
Dhw priority?Hmmmmmmh?I have to check. The circs run 24/7 for heating.I know that when not calling for domestic that the boilers are dropping way down in temp and with a call for domestic they ramp right up to 180.Without DHW priority how would it act?0 -
Pushing the Chimney Sweep Button
The button is there so the burner tech can do a test without having to turn up the TStat. It also will alert us that you are playing with our equipment(joking).0 -
Big brother Buderus
So that's why, I thought it was like a direct like to tech support or that a chimney sweep was on the way to slap my hand. lol0 -
Daaaarrrrrin
How do You Know that ???
hhhmmmmmmm ??
Scott
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"0
This discussion has been closed.
Categories
- All Categories
- 86.6K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 54 Biomass
- 423 Carbon Monoxide Awareness
- 98 Chimneys & Flues
- 2K Domestic Hot Water
- 5.5K Gas Heating
- 101 Geothermal
- 157 Indoor-Air Quality
- 3.5K Oil Heating
- 66 Pipe Deterioration
- 931 Plumbing
- 6.2K Radiant Heating
- 384 Solar
- 15.2K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 43 Industry Classes
- 48 Job Opportunities
- 17 Recall Announcements