Circulator Mounting Height
Bruce M.
Member Posts: 143
Is there an ideal mounting height for a circulator? Will mounting the circulator a certain number of inches above a manifold provive better circulation? If there is a formula, is it dependant upon the manifold diameter and the supply and return diameter?
0
Comments
-
The height of a circulator
location is irrelevant to its performance. Assuming it is pumping away from the PONPC.
It the pump sucks the water - rather than pushing it, the height of the circulator would be a very relevant consideration.
The reason for this phenomenon is the head pressure of the pump will be subtractive if it discharges into the PONPC. It will be additive if installed with the suction inlet close to the PONPC. With water temps high, the circulator will cavitate and be destroyed if it sucks water, rather than pushes it.
Dan's book "Pumping Away" is the seminal work on the topic. I urge you to buy it.
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"0
This discussion has been closed.
Categories
- All Categories
- 86.5K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 423 Carbon Monoxide Awareness
- 96 Chimneys & Flues
- 2K Domestic Hot Water
- 5.5K Gas Heating
- 101 Geothermal
- 156 Indoor-Air Quality
- 3.5K Oil Heating
- 64 Pipe Deterioration
- 928 Plumbing
- 6.1K Radiant Heating
- 384 Solar
- 15.1K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 48 Job Opportunities
- 17 Recall Announcements