vaporstat recommendation

tom_54
tom_54 Member Posts: 46
recommend a vaporstat for one pipe steam system. Can I simply take off the old pressuretrol and install the vaporstat?

Comments

  • Yes

    L 408A 1132 is 0-16 ounces

    L 408A 1157 is 0-4 PSI

    The 0-4 PSI isn't very sensetive below about 1 PSI.