Transition from copper to black pipe
Bruce M.
Member Posts: 143
On a hot water boiler return what is the best way to transition from copper to black pipe.?
0
Comments
-
0 -
a copper by male..
adapter...kpc
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"0 -
Copper to steel
with a copper to male or female sweat adapter is done all the time on hydronic and fire sprinlker systems. It's an accepted practice according to the CDA.
Some use a brass nipple for additional piece of mind. Use to to be able to find brass thread by sweat adapters. Still some small sized ones available from Barnett Brass.
I would highly recommend against dielectric unions, regardless of what an inspector may say. Go back and change them out if they are hard nosed about them. They really can't handle boiler temperatures, tend to accelerate corrosion. And are a big no no (zinc coating)in glycoled systems.
hot rod
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"0 -
Transition..
If you need to pass inspection (even with a bite in the a@@ inspector concerned with all the dielectric mumbo jumbo) the best way I've found is to install a brass ips ball valve, and screw a c x m adapter in it. Done! Robert O'Connor/NJ0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 64 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements