lochinvar boiler
tim_20
Member Posts: 41
I'm working on a lochinvar boiler for a loop for heat pumps. and from what i can find out once a year it has to have its ignition control replaced usually after snow or rain it is installed on a roof top. went today with new control would not reset replaced igniter too. check every thing i could think of gas pressure cleaned burners etc. looks like flame is not really touching hot surface ignitor,how much should it be?? today after spending two hours in a down pour it just started up. any ideas? going back in morning to do some more testing. thanks for any help. tim
If all else fails
Lochinvar does have some good tech support folks on the 800 number. Once you get throughYou might get their input. Check for clean and tight wire connections, everywhere!
Lots of times, these days, those controls have to be replaced with OEM. Off the shelf modules are not always going to work, or work properly. Same with gas valves.
hot rod
i replaced the parts with oem as they stated and it always is flame failure that the control goes off on this is my first trip to this job but due to the down pour left after it fired i haven't put any of the old controls back in yet so. the manager stated at least 7 controls and it always fired after up after replacing control until today very weird but i hope i get to the bottom of it. tim0 -
the boiler always locks out on flame failure as stated to me by maint. person. at least 7 controls. i replaced today with oem parts and it lock out on flame failure as he stated. checked as much as possible due to the down poor. he said first time it did not work after replacing control. very weird problem but i'm going back in a.m to call lochinvar.they have been called before hope i can get to the bottom of this and keep the rich people happy in their over priced condo's. tim0 -
7 controls, really
sounds like you need to get to the bottom of this. Treat the problem, not the symptom! It should not be eating parts like that, something else is going on.
It's not connected to 240V is it? Just kidding, sort of.
hot rod
nope 120 volts i guess thats why they sent me to get to the bottom maybe a big pay raise who knows.iv'e heard so much about this boiler but now it is in my palm. i hope lochinvar is a help but from what i hear they have been contacted before hope they are not hiding anything.0 -
Where there is a will...
Lochinvar, and others, do make new boilers, if they have grown weary of the inconvience
It's just money, they'll find more of it!
hot rod
Need to know what model of boiler you have.
Dave in Denver.There was an error rendering this rich post.
Lochinvar
model#? Is this set up for low temperature system? is this on the roof or protected by a penthouse? IS the wind blowing heavy during the rain & snow storms?0 -
Check the electrical connections
I had a simular problem with a unit in a pool area, after changing parts and much troubleshooting I spoke with Tech support, In my case it turned out to be the energy managment low voltage connections (which was not being used so it had a factory jumper installed) the screws were not tightened and corrosion was forming causing a voltage drop which acted like a bad control. Tighten All connection on the unit. hope that helps :-)0 -
the model is a cbn0645 s/ j974155 it is on a roof in the open with the correct cap for outdoor install. it is 7 stories up heading out now to try and solve.
tim0