steam traps
jfgh
Member Posts: 3
Is it possible to over size a steam trap? Case in question is an airhandling unit with a condensate load of 900lbs/hr at full load with a pressure diff. of 6psig. Steam is controlled via a modulating valve. Supplier is trying to sell be on a trap which is has a safety factor of almost 8. His reason is as valve modulates closed you no longer have a diff. press of 6#s. This is true but you also don't have a full condensate load either. Am I better off with a larger trap or smaller one with a safety factor of 3 or 4.?
0
Comments
-
steam trap
there is no advantage in oversizing a steam trap. air handlers are ok with a 3 to 1 safety factor. be sure you have a vacuum breaker installled. tp tunstall0 -
sizing on coils
Here's the scoop:
The temperature control valve has the capability to be 2/3's open, delivering steam at 2/3's of full load, and the coil is in a vacuum!
It doesn't matter that your steam supply is 8 psi. The valve is controlling the pressure to match the temperature it needs. If it needs 205 degree steam, it can do that!
That's why you'll see SHEMA ratings in older trap catalogs (like Dan's excellent books). Those ratings built in a 2:1 safety factor at about 1/2 psi differential, which looks like 6:1 at 8 psi.
See, the coil will be in a vacuum, the vacuum breaker will open, and you only have the static head of the water to drain the coil (hence the 1/2 psi differential).
The SHEMA ratings were an agreement by the equipment manufacturers on how to rate traps so that coils wouldn't freeze. The ratings accounted for wet steam, modulation of the valve, and a likely drop in pressure when "design days" hit. The SHEMA group are all "dead guys" now, but the lesson lives on...0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements