Taco Zone Valves

Kenny_2
Kenny_2 Member Posts: 3
When you place a Taco 3 wire zone valve in the manual position I know that the valve opens and allows water to flow. Does it also close the contact that energizes the circulator/burner relay?

Thanks,
Kenny

Comments

  • hydronicsmike
    hydronicsmike Member Posts: 855
    yes

    but it is not a dry contact, of course.

    Mike
  • Kenny_2
    Kenny_2 Member Posts: 3


    Thanks for the info
  • Ken D.
    Ken D. Member Posts: 836
    Taco

    FYI, On the Taco zone valves, the newer gold heads will bring on the boiler or circ. The older green or gold heads will not.
  • Joe Mattiello
    Joe Mattiello Member Posts: 720
    Taco Zonevalves

    The Taco Gold series zonevalves have the manual by-pass to allow water to thermo siphon through the loop for heat in the event you should have a power failure. That is what it was designed for. Some people will try to by-pass when the thermostat is still connected which is not recommended. Doing so can be a detriment to the valve, so Taco advocates removing the thermostat wire off terminal one. Additionally using the manual lever does not guaranty closure of the end switch.
    Taco, Inc.
    Joe Mattiello
    Technical Service Technician
    joemat@taco-hvac.com
    401-942-8000 X 484
    www.taco-hvac.com
    Joe Mattiello
    N. E. Regional Manger, Commercial Products
    Taco Comfort Solutions
  • Kenny_2
    Kenny_2 Member Posts: 3


    Thanks again for the additional info.