taco sr502
Options
steve_68
Member Posts: 3
Having problem with zone 1 relay chatter when priority jumper is removed (for priority). Zone 2 works fine regardless. Zone 1 works fine with jumper in place (no priority). Not the relay, short in connected load or t-stat circuit. Replaced control, same thing. Does anybody know what is going on with these things??
0
Comments
-
Wiring
My guess is that you have the incomming line voltage wrong.
White goes to "N" Neutral and Black goes to "H" Hot. My guess it that you have power/black to "P".
Tim D.0