65 ft of fintube?
powerhead
Member Posts: 26
I once heard of a rule of thumb that you can't run more than 65 ft of 3/4 fintube per zone or else you will "run out" of heat. I think this had something to do with maximum gpm through a 3/4 pipe. Does anyone know how this rule works? Does the 65 ft include pipe and fin or just fin alone?
0
Comments
-
Yup...
that there would be the finned tube limitation for 3/4" pipe at a 20 degree delta t...
65 feet times 550 btu/foot = 35,750 btuH. That, divided by 10,000 (btuh 1 gpm will deliver at a 20 degree delta T) = 3.57 GPM which is pert near the maximum recommended gpm through a 3/4" pipe based on silent operation.
Powerhead, thats a new name. Welcome to the Wall. Hang out and learn something, will ya:-)
ME