primary/secondary or heat exchanger
pat_3
Member Posts: 89
when doing a small radiant system that will be tied into an existing hot water {high temp} heating system,do most radiant contractors repipe the boiler primary/secondary or use some sort of heat exchanger to protect the boiler from low temp return water from radiant side of system?
There was an error rendering this rich post.
0
Comments
-
What I do...
is pretty simple...I pipe a another zone as a supply and return w/ a circulator or ZV, this is my "primary"loop. Then take off two tees, close spaced as my secondary loop to usu. a sparco mixing valveand another circulator. This gives boiler protection and negates the boiler repipe.kpc
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"0 -
kevin
thanks for your input...i cant believe i never realized such an easy way to protect the boiler.....There was an error rendering this rich post.
0 -
sometimes with a small
load radiant add on, suspended tube running the same temperatures as the baseboard is not a bad system.
Plates are great, but there are times when simple is sufficient
Here are some other ideas
http://www.pmmag.com/CDA/ArticleInformation/features/BNP__Features__Item/0,2379,62497,00.html
hot rod
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"0 -
Taco RMB
Pat,
You could also look at a taco RMB, it was designed just for the job you have. It's a slick package with 2 pumps and 4 connections. The one pump and controls work as a variable speed injection pump and the other is the radiant zone circulator. The controls do outdoor reset on the temperature delivered to the radiant slab (better than a static temp IMO.)
You hook the supply side up as standard P/S plumbing. The secondary side goes right to the radiant loops, zone valves, etc. People who have installed them love them.
jerry
0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements