piping for steam relef valve exaust

Dave Bush
Dave Bush Member Posts: 155
I'm involved with this little project, too...

I've got my red pen out, Scott.:=}

Welcome

It looks like you're new here. Sign in or register to get started.

Comments

  • Scott Price_2
    Scott Price_2 Member Posts: 6


    I need help in locating info or specs for piping exaust steam
    outside the building. This is a 1200 lb per hr boiler.
    Our state boiler code requires exausting to outside anything
    over500 lb per hr. thanks
  • Kevinj
    Kevinj Member Posts: 67
    vent

    Check with your inspector, they will probably want it vented to ASME standards with drip pan and drain.
  • Tony Conner_2
    Tony Conner_2 Member Posts: 443
    You Likely Won't...

    ...find much in the way of specifics because there are just too many variables. The wording will likely just be something to the effect that "...the discharge piping will be properly designed (sized, layed-out, and supported), and discharges to a safe area."