piping for steam relef valve exaust

Dave Bush
Member Posts: 155
I'm involved with this little project, too...
I've got my red pen out, Scott.:=}
I've got my red pen out, Scott.:=}
0
Comments
-
I need help in locating info or specs for piping exaust steam
outside the building. This is a 1200 lb per hr boiler.
Our state boiler code requires exausting to outside anything
over500 lb per hr. thanks0 -
vent
Check with your inspector, they will probably want it vented to ASME standards with drip pan and drain.0 -
You Likely Won't...
...find much in the way of specifics because there are just too many variables. The wording will likely just be something to the effect that "...the discharge piping will be properly designed (sized, layed-out, and supported), and discharges to a safe area."0