Buderus POST PURGE
RoosterBoy
Member Posts: 459
Hi I have a buderus G115 28 with a power Venter and was wondering what buderus recommends right now the powervent has a post purge set to 5 mins is this ok or should we up it to 10 min
thanks
thanks
0
Comments
-
Hi,
What burner are you running? Sidewall vent or vertical vent?
Ron0 -
im runing the riello 40 f3 with a swg-5s power venter
http://www.fieldcontrols.com/swg.html
it's a sidewall0 -
I'm surprised that you are not running a BF3. It would directly side vent if you aren't too far from the wall.
I run a 2 minute post purge on my G115/21 with a BF3 and about 7 feet of vent.
Ron0 -
yea I just think that a power Venter was nicer and that it will hold up better in the wind i had a power vent on my furnace for 5 years with no problem
I just bough this one with this new boiler and I got it in stainless steel
hay ron id love to see a picture of your setup with the bf3
thanks0 -
Hi Roosterboy,
No Pictures allowed until I clean the crap out of the basement. ;-)
Ron0 -
Post Purge
A two minute post purge will be sufficient to pull the gases out of the boiler and cool down the head of the burner.0 -
Come On!
your basemnt CAN'T be any worse than any of the ones we have seen here. kpc
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 64 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements