STEAM BOILER -BANGING PIPES

HAVE A STEAM BOILER 1LB RUNNING PRESSURE -AFTER 3 OR 4 HOURS WHEN ALL ZONE VALVES ARE SATTISFIED THE PIPES START BANGING ALOT

Comments

  • DanHolohan
    DanHolohan Member, Moderator, Administrator Posts: 16,601
    Please read this

    The Challenge of motorized valves

    It pays to wander off the Wall.
    Retired and loving it.
  • Fred Harwood
    Fred Harwood Member Posts: 261
    banging

    Closed zone valves can create a large vacuum, that can suck boiler water up into the mains. You may need to install vacuum breakers after the valves.
  • Banging because of closed zone valves

    Firstly in any two pipe steam system with zone valves a steam vacuum breaker should be installed on the boiler trim.

    As to installing vacuum breakers on the steam system I don't think you want to do that.

    Here is a couple of questions for you.

    Does the steam system have a dry return?
    Does the system have a wet return and a master steam trap?
    Does the system have a condensate receiver or boiler feed pump set?
    Does the system have a vacuum pump and tank set in it?

    Typically, in two pipe steam systems with zone valves an equalizing line fron the steam main to the main return is installed.

    The equalizing line prevents the steam side of the system from developing a greater vacuum than the return side of the system.

    As steam condenses in the steam main and the steam main cools when the zone valve is closed the pipng system can go into vacuum. Equalizers on the piping system and vacuum breakers on boilers generally cure this problem.

    Jake