Digital Thermostate dosen't Work with 356 mixing Control
Options
Ram_3
Member Posts: 1
I cant get a honywell T8400B Digital T stat To controll the Tekmar 356 mixing controll. I plug the T stat in, and the 356 Calls for mixing demand with the t Stat in the off position. The 356 serve's only one mixed Zone. I have the T stat wired derectly to the 356 conrol red to T White to Com., the 356 Is powerd by the 24 volt power source from a taco SR504 EXP zone pump swithching relay controll box. Im able to get Old School Mercury T stat to work fine. What's Up with this.
0
Comments
-
tstat
you need an isolation relay,simple cube relay will work, isolate the 24 volts0 -
Power stealing tstat
This is a known issue. Power stealing thermostats require current to power the thermostat even when the thermostat is not calling for heat. The 356 registers this "trickle current" as a mix demand.
This can be corrected by either connecting an isolation relay to isolate the 356 from the thermostat or it has been found in some cases that a 1000 ohm resistor in parallel to the "T" and the "Com" terminals will also correct this.
If you have any questions, please call tekmar tech support.
Jay www.tekmarcontrols.com 250-545-77490 -
The 8400
These stats came with the required resistor if I recall. It should be in the box. If that doesn't do it, you'll have to do the isolation relay thing.0
This discussion has been closed.
Categories
- All Categories
- 87.3K THE MAIN WALL
- 3.2K A-C, Heat Pumps & Refrigeration
- 61 Biomass
- 429 Carbon Monoxide Awareness
- 120 Chimneys & Flues
- 2.1K Domestic Hot Water
- 5.8K Gas Heating
- 115 Geothermal
- 166 Indoor-Air Quality
- 3.7K Oil Heating
- 77 Pipe Deterioration
- 1K Plumbing
- 6.5K Radiant Heating
- 395 Solar
- 15.7K Strictly Steam
- 3.4K Thermostats and Controls
- 56 Water Quality
- 51 Industry Classes
- 50 Job Opportunities
- 18 Recall Announcements