Piping a wall hung boiler

I haven't run across this yet but I am sure that I will.

It seems that some of the wall hung and other high tech boilers come with internal circulating pumps some even controlled by the boilers logic. How do you deal with "Pumping Away" when the pump is inside of the boiler package?

Ron

Comments

  • hydronicsmike
    hydronicsmike Member Posts: 855
    Primary / Secondary

    Pipe the wall hung Boiler into the System Loop with two closely spaced tees (also called Primary/Secondary) or Low Loss Headder to isolate the Boiler from the System Loop. Let the Wall Hung Boiler operate the Boilers Pump (in most cases) and take over on the System Loop side.

    In most cases, the Boiler Pump is not the right Pump for the System, but for the Boiler alone.

    For multiple wall hung Boilers, use the Paralell Primary/Secondary Piping arrangement.

    Hope this helps.

    Mike
  • Ron Schroeder_2
    Ron Schroeder_2 Member Posts: 176


    Hi Mike,

    What kind of pump do they use? A normal flanged one?

    One thing that I briefly thought of was to put a tee on the pressure gauge fitting and add the expansion tank there.

    Ron
  • Dan_16
    Dan_16 Member Posts: 11


    On my trinity boiler I used a taco 011 for the primary with 2 oo7 pumps for my secondaries. I installed them with the isloator flanges with built in ball valves. In regards to the expansion tank I used a 1 1/4 spirovent which has a 1/2" fta and hung my tank below inside of the primary loop and then tied my make up between the two with a T.
  • Steve Eayrs
    Steve Eayrs Member Posts: 424
    Is this a exp. tank location question?

    Or a pump question?

    Some of these boilers (Vitodens for instance), have the internal pump on the supply, and if the floe rate is within the specs. the boiler pump can handle it, and ept. tank will most likely be on the return.

    Others have already mentioned the p/s piping/pump needed if the demand can't be met by the internal boiler pump.


    Steve
  • Ron Schroeder_2
    Ron Schroeder_2 Member Posts: 176


    It sounds like relying on the head pressure of the primary loop being so low, it doesn't matter where in the primary loop the expansion tank is.

    Ron
  • Uni R
    Uni R Member Posts: 663
    Piping a wall hung boiler

    The expansion tank doesn't even need to be in the primary loop. Check out the installation manual for an Ultra and it is on the secondary loop.